The fire resistance rating of a separation extending 10 ft (3050 mm) from a set of stairs shall not be required to exceed 1 hour where openings have a minimum of what fire protection rating?

Suggested Answer: B Vote an answer

Comprehensive and Detailed Step-by-Step Explanation:
Fire Resistance and Stair Separation:
According to NFPA 101 (Life Safety Code), Section 7.2.2.5, where a fire-rated separation extends 10 feet from a stair enclosure, the separation fire resistance does not need to exceed 1 hour if the openings have a ½-hour fire protection rating.
Why ½ Hour is Acceptable:
Openings with a ½-hour fire protection rating are sufficient to limit fire spread in lower-risk scenarios.
This exception applies to areas where the separation is minimal but still provides adequate protection to occupants using the stairway.
Other Options Explained:
Option A (2 hour): Not required for this scenario.
Option C (1 hour): The wall may be 1 hour, but the openings need only ½ hour.
Option D (1 ½ hour): Exceeds the requirements.
Summary:
Openings must have a minimum ½-hour fire protection rating where the fire resistance-rated separation extends 10 feet from a set of stairs.

by June at May 13, 2026, 12:02 PM

Comments

Chosen Answer:
This is a voting comment (?) , you can switch to a simple comment.
Switch to a voting comment New
Nick name: Submit Cancel
A voting comment increases the vote count for the chosen answer by one.

Upvoting a comment with a selected answer will also increase the vote count towards that answer by one. So if you see a comment that you already agree with, you can upvote it instead of posting a new comment.