Exam CFI-I Topic 3 Question 37 Discussion

Actual exam question for NFPA's CFI-I exam
Question #: 37
Topic #: 3
What is the minimum fire protection rating for a fire door in a 2-hour fire resistance-rated assembly that protects a refuse chute?

Suggested Answer: C Vote an answer

Fire doors in fire resistance-rated assemblies must have a fire protection rating proportionate to the rating of the assembly they protect. According to NFPA 80, Standard for Fire Doors and Other Opening Protectives, and NFPA 101, Life Safety Code:
For a 2-hour fire resistance-rated assembly, the fire door protecting an opening (like a refuse chute) must have a minimum fire protection rating of 1½ hours (90 minutes).
The reduced rating for the door (relative to the wall) is allowed because doors are tested to prevent fire spread through openings for their specified rating period.
½ hour (A) and 1 hour (B) are insufficient for a 2-hour assembly.
2 hours (D) exceeds the requirement but is unnecessary unless specified for high-risk openings.
Reference:
NFPA 80, Table 4.2.1.1: Fire door ratings based on fire resistance-rated assemblies.
NFPA 101, Section 8.3.4.2: Fire door requirements for vertical openings like refuse chutes

by Emily at Mar 08, 2026, 02:51 PM

Comments

Chosen Answer:
This is a voting comment (?) , you can switch to a simple comment.
Switch to a voting comment New
Nick name: Submit Cancel
A voting comment increases the vote count for the chosen answer by one.

Upvoting a comment with a selected answer will also increase the vote count towards that answer by one. So if you see a comment that you already agree with, you can upvote it instead of posting a new comment.