Extra high temperature sprinklers should be tested every

Suggested Answer: A Vote an answer

Extra-high, very extra-high, or ultra-high temperature, solder-type fire sprinklers exposed to very hot environments-test every 5 years Some fire sprinkler environments, like industrial facilities, are extremely hot, and sprinklers with very high, very extra-high, and ultra-high temperature ratings are used above equipment like ovens, furnaces, and boilers. The ambient heat can cause the meltable solder to migrate in fusible-link fire sprinklers (the ones without glass bulbs), affecting their ability to activate. Where these models are in such environments for at least five years, fire sprinkler testing must be done every five years:
From the 2023 edition of NFPA 25 5.3.1.1.1.3* Where solder-type sprinklers with a temperature classification of extra high [325°F (163°C) or greater] are installed and exposed to semi-continuousto continuous maximum allowable ambient temperature conditions for 5 years, one of the following shall occur: (1) The sprinklers shall be replaced. (2) Representative samples of the sprinklers shall be tested and then retested every 5 years.

by Marlon at Feb 18, 2025, 05:38 AM

Comments

Chosen Answer:
This is a voting comment (?) , you can switch to a simple comment.
Switch to a voting comment New
Nick name: Submit Cancel
A voting comment increases the vote count for the chosen answer by one.

Upvoting a comment with a selected answer will also increase the vote count towards that answer by one. So if you see a comment that you already agree with, you can upvote it instead of posting a new comment.