Exam CWBSP Topic 3 Question 20 Discussion

Actual exam question for NFPA's CWBSP exam
Question #: 20
Topic #: 3
What is the minimum sprinkler operating pressure and minimum sprinkler flow rate required for an ordinary hazard group 1 sprinkler system with K8 (115) sprinklers spaced 110 ft2 (10.2 m2) per sprinkler?

Suggested Answer: C Vote an answer

For an Ordinary Hazard Group 1 area using K8 (115) sprinklers spaced at 110 ft² per sprinkler, a minimum operating pressure of 7 psi and a flow rate of 21.2 gpm would typically be required. This ensures sufficient coverage and water delivery for the density and area covered by each sprinkler.
References: General guidelines from NFPA 13 on sprinkler system design criteria, including minimum operating pressures and flow rates for different hazard classifications.

by Uriah at Feb 28, 2025, 06:37 AM